Servery in a Commerical Bldg

Status
Not open for further replies.

jmd445

Senior Member
I have a servery in a commercial building where food is sold but not necessarily prepared (hence the servery and not kitchen).

There is a 20A 208V twistlock recept. 3 ft from a sink above counter top height. This will serve coffee urns. Is GFI protection required?

Jim
 
jmd445 said:
I have a servery in a commercial building where food is sold but not necessarily prepared (hence the servery and not kitchen).

There is a 20A 208V twistlock recept. 3 ft from a sink above counter top height. This will serve coffee urns. Is GFI protection required?

Jim

Is GFI protection ever required on a 208V outlet?
 
jmd445 said:
There is a 20A 208V twistlock recept. ...
Jim

GFCI protection NOT required.

210.8(B)
Other Than Dwelling Units.
All 125-volt, singlephase, 15- and 20-ampere receptacle....
 
Status
Not open for further replies.