Jpflex
Electrician big leagues
- Location
- Victorville
- Occupation
- Electrician commercial and residential
What I don’t understand is how feeders or service conductors can be protected by the next larger standard size breaker when the ampacity of the feeder or service does not correspond to a standard breaker when not more than 800 amperes
I say this because one of the requirements is that the feeder:
1) conductors being protected are NOT part of a branch circuit supplying more than one RECEPTACLE FOR CORD AND PLUG CONNECTED PORTABLE LOADS 240.4 (B)
Therefore, every dwelling i know has the feeders or services part of such receptacle loads. The services and feeders have continuity to multiple receptacle loads via main panel and branch circuits
I say this because one of the requirements is that the feeder:
1) conductors being protected are NOT part of a branch circuit supplying more than one RECEPTACLE FOR CORD AND PLUG CONNECTED PORTABLE LOADS 240.4 (B)
Therefore, every dwelling i know has the feeders or services part of such receptacle loads. The services and feeders have continuity to multiple receptacle loads via main panel and branch circuits