jbelectric777
Senior Member
- Location
- NJ/PA
For everyone who uses the NEC and is subject to inspection, pass this on to a fellow installer, it may save a lot of trouble and $$$$$. Type SEU & SER usually used in dwellings has to be de rated if used for non dwelling service entrance. An example is 4/0 aluminum and a 200 amp breaker in a dwelling cant be used for a commercial office building because a 4/0 aluminum isnt rated for it. It happened today to a nice guy I know, his plans that went through my review passed because the architect (or his sub contracting engineer) knew the rules exception for dwellings, now he has to change either 5 breakers or all the SER his electricians already installed. Its not such a big deal to me in theory as most of you would agree but its code, and at the end of the day the bottom line is someone fooged up!, and I cant cover for em... Always be sure to read your plans and not assume you think you know if your not sure, and if your not sure call your boss or even your local inspector, thats what he's there for..... I hope this helps someone from not running into the same problem, and if it was ever discussed before here then good and take it as a simple reminder....... I hope everyones Thanksgiving was a good one! And Merry Christmas and a Happy, safe new year to everyone if I dont get in the forum before the holidays.....