Your point directly nails the argumentative nature of this issue.
If, as you say, you want to maintain the same ampacity, then you would need to increase the interior SE to attain the same ampacity, however, literally 215.2 would allow the smaller cable.
The 338.10 vs 215.2/310.16 situation, unfortunately, is interpreted differently in different areas.
If, as you say, you want to maintain the same ampacity, then you would need to increase the interior SE to attain the same ampacity, however, literally 215.2 would allow the smaller cable.
The 338.10 vs 215.2/310.16 situation, unfortunately, is interpreted differently in different areas.