V vasparky Member Mar 17, 2004 #1 I realize that #2 seu is rated for 90 amps so I'm assuming that it is not suitable to use it as 100a service cable? does it come in copper would it then be rated for 100A?
I realize that #2 seu is rated for 90 amps so I'm assuming that it is not suitable to use it as 100a service cable? does it come in copper would it then be rated for 100A?
tom baker First Chief Moderator & NEC Expert Staff member Location Bremerton, Washington Occupation Master Electrician Mar 17, 2004 #2 Re: service cable ????? See 310.15 (B)(6) for dwelling services ampacities, make sure you have the errata for this section, its available at www.necdirect.org