Background:
Existing 2600sf building. Adding 1400sf (4000sf total).
Existing service is (2) 200A panels with mains, 120/240V, 1-phase. Utility has the peak at 50A.
Our task was to compare bringing gas to the building or keep the heat pump type design.
We have 13.5KW (56A) of auxiliary electric heat in the building. This is non-peak for gas heat (summer is peak load), but can't be deducted with a heat pump.
Our calculations:
Gas heat: connected=61KVA, demand=47.5KVA (200A)
Heat pump connected=91KVA, demand=93KVA (390A)
I tweaked some loads and got each panel to be exactly 200A demand. I just realized I forgot a load making one panel 205A.
Am I missing something in the NEC?
Typically the code calculation is about 1.75 times of what's needed. In this case, I'm at 5 times!
Any help would be greatly appreciated.
Joe