Re: Service Calculation
Here's my shot at it.
Lighting (1500 x 3) = 4500
Outlets (20 x 180) = 3600
Furnace (20 x 120) = 2400
A/C (40 x 240) = 9600
Heat = 0 (non-coincident with A/C)
Tanning Bed #1 (45 x 220) = 9900
Tanning Bed #2 (26 x 220) = 6240
Tanning Bed #3 (21 x 220) = 5040
Tanning Bed #4 (21 x 220) = 5040
Tanning Bed #5 (16 x 220) = 3840
Sign = 1200
Show Window (8.5 x 200) = 1700
Total = 53,060 VA
Total = 221 amps.
You had some math errors in the earlier calculation. Also, you came up with the 203.4 number before you acknowledged the need to add the sign and the show window.Originally posted by buggaboo14: With all the info given, I have a calculation of 203.4 amps. Could someone check my calculations?
Here's my shot at it.
Lighting (1500 x 3) = 4500
Outlets (20 x 180) = 3600
Furnace (20 x 120) = 2400
A/C (40 x 240) = 9600
Heat = 0 (non-coincident with A/C)
Tanning Bed #1 (45 x 220) = 9900
Tanning Bed #2 (26 x 220) = 6240
Tanning Bed #3 (21 x 220) = 5040
Tanning Bed #4 (21 x 220) = 5040
Tanning Bed #5 (16 x 220) = 3840
Sign = 1200
Show Window (8.5 x 200) = 1700
Total = 53,060 VA
Total = 221 amps.