tyha

Senior Member
Location
central nc
had a call come in at a residence - we dont do residential but this is a special customer. lighting struck near thier house and power went out. when it came on none of thier 220 loads worked. HWH, Heat pump. Im thinking a leg dropped. what is the most common answer?
 
Fried one leg, fried main breaker. I've seen one leg of a main breaker trip without dragging the other along for the ride, too. Try resetting/cycling the main. If you ask me, the whole place should be meggered too. Verify all GEC connections as still being solid (and, in fact, not fused off).
 
080706-2110 EST

If the main panel has main fuses, then one might be blown. But why might be a question if there is no apparent damage in the home.

Obviously use a meter to check the incoming line voltages at the main panel.

.
 