When changing a 100 amp to a 200 amp service does the utilities upgrade/ increase size of thier service drop conductors?
I have often seem contractors just tie the new 200 amp conductors to the existing wires
We temp it back and if the power company decides they need new wires then that is their job. They have different guidelines then we do as they do not use the NEC.
I understand they don't follow the NEC but
Do you know what size wire, free air can be used for a 200 amp service? Curious why they wouldn't change it out?
Curious why they wouldn't change it out?
Because it costs money.:happyyes:
How about when you went from 100 amp single phase to 200 amp three phaseI've never once seen Nevada Energy in Las Vegas area change the overhead wires when I did a 100A to 200A service panel upgrade. I've also never had my customer call back about any issues.
I've never once seen Nevada Energy in Las Vegas area change the overhead wires when I did a 100A to 200A service panel upgrade.
I added some HVAC load to a school one time. POCO had a run of 3 inch PVC with 500 aluminum to the building and CT metering at the building. Told them what I would be adding for load, I know they took into consideration the peak demand, how many hours it may run that way, and how many hours til it would have to cool down before next peak demand cycle. They decided to replace 500 aluminum with 500 copper based on what they figured, and upgrade 75 kVA single phase transformer to a 100 kVA. This conductor ultimately supplied 800 amps worth of multiple service disconnecting means on two separate buildings. I don't recall what actual NEC load calc would have been - too long ago, but would guess maybe 500-600 amps.Ditto.
If they are right say 95% or more most times, why would they?
Same for trannies.
The odds are it will okay, they know this from experience.
How about when you went from 100 amp single phase to 200 amp three phase![]()
When changing a 100 amp to a 200 amp service does the utilities upgrade/ increase size of thier service drop conductors?
I have often seem contractors just tie the new 200 amp conductors to the existing wires
Why they just added one new wire and one transformer!![]()
Then it probably wouldn't work since it's residential we're talking about.How about when you went from 100 amp single phase to 200 amp three phase![]()
Then it probably wouldn't work since it's residential we're talking about.
Unless you tell them you are adding significant load, like instantaneous electric water heating or electric heat they assume it will have about the same demand it had before.
Gadfly, our POCO doesn't charge anything for upgrades, likely because they know they'll be selling more power. Also, it sounds like 100a would have been plenty, although the labor is the same either way.