electricguy61
As a preface, I'm in CA, so we are just now adopting the 2014 code.
I'm getting ready to replace a 100 amp residential service (usually would replace with 200amp, but PG&E has some strange requirements for upgrades adjacent to gas meters. They'll let you install the same size, but not upgrade).
Just for hoots, I looked up the minimum wire size in my new 2014 NEC Handbook. Whereas in the 2011 handbook, Table 310.15(B)(7) clearly gave you wire sizes for services, in the 2014 there are only formulas (basically you can use wire ampacity 83% of the service rating).
Which at 75 degrees C would be 83 amps for a 100 amp service (#4 THHN), 104 amps for a 125 amp service (#2 THHN), 125 amps for a 150 amp service (#1 THHN), and 166 amps for a 200amp service (2/0THHN).
Which is the same as the previous table, only harder to figure out.
Anyone know why the powers that be removed the simpler to read table? Or if my calcs above are incorrect, please inform me.
Thanks
Thanks