FREEBALL
- york pa usa
Im looking at a job where the underground service needs to be moved so a garage can be built beside the customers home. Met Ed said they would consider taps in the secondary underground, we were going to install a 200 amp meter at the garage and reefed house, then we decided it would be best to install a 320amp meter at garage and feed the house as a service which they agreed is acceptable, they said they would have to charge 700 dollars to feed the 320 meter because conductors have to be sized to the meter. The customer agreed, The total load is 108 amps with the add on garage, everything is gas. Anyway Id like to reuse the existing 3 wire service underground to the house from the new meter location. The length is approx. 130 ft from new meter to existing meter on house. The service conductors at the existing meter base will not be long enough to extend into the panel. Can I bond an enclosure there to the neutral since it is still service conductors, and no parallel feed back to meter? Id like to keep from having to trench an additional 100 feet and resupply with 4 wire from the panel as a feeder. That is my question. PS I looked into PVC enclosures for a pvc enclosure the size I need for the conduits entering would be an 18x18 and well carlon only makes a 24x24 at 370.00 so a metal enclosure is what I would need.
Thanx
Jeff
Thanx
Jeff