Service Conductor wiring trough

Status
Not open for further replies.

Johnhall30

Senior Member
Location
New Orleans, LA
Occupation
Engineer
Here is a service for a residential apartment building, with four 800 Amp disconnects feeding different meter centers, and a house meter CT cabinet feeding two 400 Amp disconnects.

Everything ahead of the service disconnects is considered service conductors, and does not apply to the tap rules in the NEC. Does anyone see a code violation in this service configuration containing two wiring troughs?


Document1.jpg
 

Strathead

Senior Member
Location
Ocala, Florida, USA
Occupation
Electrician/Estimator/Project Manager/Superintendent
Here is a service for a residential apartment building, with four 800 Amp disconnects feeding different meter centers, and a house meter CT cabinet feeding two 400 Amp disconnects.

Everything ahead of the service disconnects is considered service conductors, and does not apply to the tap rules in the NEC. Does anyone see a code violation in this service configuration containing two wiring troughs?


View attachment 2558536
Check your utility. Many will require a single switch not a service disconnect for over a certain amps. Here it is 800 amps. Over current protection no required.
 