al Senior Member Location Minnesota Nov 2, 2008 #1 Must service conductors be either: a) Service Drop b) Service entrance c) Service Lateral, or can they be just service conductors and not be any of the three above?
Must service conductors be either: a) Service Drop b) Service entrance c) Service Lateral, or can they be just service conductors and not be any of the three above?
mdshunk Senior Member Location Right here. Nov 2, 2008 #2 Anything before the first NEC compliant overcurrent device is a service conductor. The more descriptive you get with the term, the more specific the location of that section of service conductor referenced.
Anything before the first NEC compliant overcurrent device is a service conductor. The more descriptive you get with the term, the more specific the location of that section of service conductor referenced.