I was looking at the Graphic that Makes it illegal to install Service Conductors in the same raceway as Feeder or Branch Conductors saying that if there was a fault it would bypass the service disconnect and energize one phase of a panel that it was feeding and the circuits connected to that phase.This would have to be a perfect scenario where if there was a fault, the fault would have to be between a Service Conductor and a Feeder Conductor of the same Phase, Otherwise something would blow up or the primary fuses would most likely blow for going phase to phase.Whats the chances of a fault occuring in a Service raceway where the fault would cross only a feeder conductor of the same phase? (Not Likely).One could argue the same point on a Feeder and Branch circuit scenario. Take a 500 mcm feeding a 400amp panel and a #12 Branch circuit out of that same panel. If for some reason the #12 dug into the 500 MCM Miraculously on the same phase, The #12 would be fused at 400 amps and would not be able to be shut off by the 20 amp breaker.Or if it dug into a 500 mcm on a different phase something would blow.Just another arguable fact of where to draw the line on some things.
There are still a ton of up and down services being built.
There are still a ton of up and down services being built.