Encasement in 2 inches or more of concrete or other masonry generally is considered outside the building even if not within the outer envelope of the building.Well...I'll debate this a little further...
Yes, I see your point related to the added language in the 2014 NEC 230.6(5)...
But, inside outer building surfaces constructed similar to this that comply with 230.6(2) would allow any service conductors suitable such as RMC, IMC, EMT, ENT, SE, MC, PVC...to be routed through the exterior wall envelope of a building.
View attachment 16138
Also note that 230.6(5) only applies to installations to accommodate the overhead clearance rules of 230.24