Code:Your second option you mention of changing the service panel would be a much bigger job that using a branch circuit style ATS. Some smaller ones are pre wired. But even if not you don't actually reroute the branch circuits they stay in the meter/main and a jumper is run out for each to the ATS and back, no change for N/G bonding required either.
Just to confirm all of the nuetrals and grounds need to originate from the same panel as the hots, correct? Whats the NEC section for that?
I can combine grounds and bring over a #8 or #6, correct? How do I size that according to NEC?
Thanks again
Sent from my SM-N960U using Tapatalk
I guess 300.3(B) would answer that question
(B) Conductors of the Same Circuit.
All conductors of the same circuit and, where used, the grounded conductor and all equipment grounding conductors and bonding conductors shall be contained within the same raceway, auxiliary gutter, cable tray, cablebus assembly, trench, cable, or cord, unless otherwise permitted in accordance with 300.3(B)(1) through (B)(4).