230.3 says this:
If you have a 400A service with two 200A disconnects outside, one disconnect is for the building it's mounted on, the other is for a separate building. Would 230.3 prevent running the conductors for the 2nd building through the 1st building?
Before anyone says or mentions it, the 2nd building will have a MB panel. The feed will enter it from the outside back-to-back to the panel.
230.3 One Building or Other Structure Not to Be Supplied
Through Another. Service conductors supplying a
building or other structure shall not pass through the interior
of another building or other structure.
If you have a 400A service with two 200A disconnects outside, one disconnect is for the building it's mounted on, the other is for a separate building. Would 230.3 prevent running the conductors for the 2nd building through the 1st building?
Before anyone says or mentions it, the 2nd building will have a MB panel. The feed will enter it from the outside back-to-back to the panel.