M mhayes Member Jun 30, 2009 #1 If I run PVC conduit from the building mounted meter socket underground to the utility pole and rise up the pole with GRC, do I need to bond this to the main service grounding conductor?
If I run PVC conduit from the building mounted meter socket underground to the utility pole and rise up the pole with GRC, do I need to bond this to the main service grounding conductor?