Pierre C Belarge
Senior Member
- Location
- Westchester County, New York
The NEC and local laws generally follow the same requirements for this topic.
The location of a service disconnect can be located outside of a building or structure, as per: (this requirement is not occupancy sensitive, it relates to all services, in all building Types)
"230.70(A)(1) Readily Accessible Location.
The service disconnecting means shall be installed at a readily accessible location either outside of a building or structure or inside nearest the point of entrance of the service conductors."
Although the NEC does not address this, I am curious how some feel about the following question.
1. How far from the building or structure can the outside service disconnect be installed, before it would be considered a separate structure?
The separate structure issue brings about some changes in the grounding scheme(s), both in Part III of Article 250 and Section 250.32.
A second question - for thought....
2a. If one grounds the outside service disconnect to the structure water pipe/steel/CEE, etc... is it part of the building and not a separate structure??
2b. If one grounds the outside service disconnect to ground rods only and not to the structure water pipe/steel/CEE, etc..., is it not part of the building and would be considered as a separate structure?
The location of a service disconnect can be located outside of a building or structure, as per: (this requirement is not occupancy sensitive, it relates to all services, in all building Types)
"230.70(A)(1) Readily Accessible Location.
The service disconnecting means shall be installed at a readily accessible location either outside of a building or structure or inside nearest the point of entrance of the service conductors."
Although the NEC does not address this, I am curious how some feel about the following question.
1. How far from the building or structure can the outside service disconnect be installed, before it would be considered a separate structure?
The separate structure issue brings about some changes in the grounding scheme(s), both in Part III of Article 250 and Section 250.32.
A second question - for thought....
2a. If one grounds the outside service disconnect to the structure water pipe/steel/CEE, etc... is it part of the building and not a separate structure??
2b. If one grounds the outside service disconnect to ground rods only and not to the structure water pipe/steel/CEE, etc..., is it not part of the building and would be considered as a separate structure?