GWITT said:
What Is The Code For Having Anything Mounted Directly Under A Service Disconnect.

The rule would be found in 110.26(A).

In a nut shell nothing can be under the service disconect except other electrical equipment that does not extend more than 6" from the face of the disconect.
 