G GWITT Member Dec 13, 2006 #1 What Is The Code For Having Anything Mounted Directly Under A Service Disconnect.
iwire Moderator Staff member Location Massachusetts Dec 13, 2006 #2 GWITT said: What Is The Code For Having Anything Mounted Directly Under A Service Disconnect. Click to expand... The rule would be found in 110.26(A). In a nut shell nothing can be under the service disconect except other electrical equipment that does not extend more than 6" from the face of the disconect.
GWITT said: What Is The Code For Having Anything Mounted Directly Under A Service Disconnect. Click to expand... The rule would be found in 110.26(A). In a nut shell nothing can be under the service disconect except other electrical equipment that does not extend more than 6" from the face of the disconect.