D dave121 Member Location Central Wisconsin Apr 18, 2008 #1 If a VSD is rated at 180 amps, does the disconnect ahead of the drive need to be 115% larger, per Art.430.128, meaning the disconnect has to be rated at at least 207 amps?
If a VSD is rated at 180 amps, does the disconnect ahead of the drive need to be 115% larger, per Art.430.128, meaning the disconnect has to be rated at at least 207 amps?
bob Senior Member Location Alabama Apr 19, 2008 #2 Yes. So you will need a 225 amp disc. Any problem with this?
D dave121 Member Location Central Wisconsin Apr 19, 2008 #3 No problem at all, just wanted to know that I was understanding the code properly so I can get the correct equipment in place. Thank you.