don_resqcapt19 said:The meter may be the service point. In this area it is for underground services, but not for overhead services. For overhead services, the service point is where the utility service drop connects to the wires comming out of the weatherhead. In the case cited by the original poster, I would expect that the meter would be the service point, but even if it is, the code does not require that the service disconnect be installed at the service point.
Even though the meter is at a structure, the conductors do not supply or pass through the structure, so I don't see any way the code requires a disconnect in this case.