I understand the ruling for service disconnects being located in the same location and not more than 6 grouped together. I have an instance where a building is under single management, has a privately owned substation, and has a maintenance department. This existing building has a main distribution panel feeding the building from a transformer. This transformer is fed by a high KV Switch. The facility added a chiller plant for cooling, they added another transformer, and a second high KV switch beside the first. The inspector is telling us we must have the two separately derived system disconnects grouped together. 3/4 the building is disconnected by the first MDP and the other 1/4 by the second MDP in another part of the building. The questions I have are:
#1. Wouldn't the 2 High KV switches be considered as a disconnecting means for each part of the building?
#2. If there are documented safe switching procedures established and maintained for disconnection, and the establishment is monitored by qualified personnel (such as the manitenance department), Wouldn't this be an exception to the disconnecting means being grouped in the same location? If not would these documented procedures allow the high KV switches to be used as the disconnecting means? The section I am reading is 225.32 Exc. #1
#1. Wouldn't the 2 High KV switches be considered as a disconnecting means for each part of the building?
#2. If there are documented safe switching procedures established and maintained for disconnection, and the establishment is monitored by qualified personnel (such as the manitenance department), Wouldn't this be an exception to the disconnecting means being grouped in the same location? If not would these documented procedures allow the high KV switches to be used as the disconnecting means? The section I am reading is 225.32 Exc. #1