Service drop clearance from pool

Merry Christmas
Status
Not open for further replies.

smallfish

Senior Member
Location
Detroit
Service drop conductors to a residence on a small lot are within the required 22.5 feet clearance of the water level of a permanently installed above-ground swimming pool specified in Table 680.8. These clearances consider such factors as the use of skimmers with aluminum handles and their possible contact with overhead conductors. This pool was installed without a permit. Must this clearance be adhered to or can this distance be shortened? Thanks
 
smallfish said:
Service drop conductors to a residence on a small lot are within the required 22.5 feet clearance of the water level of a permanently installed above-ground swimming pool specified in Table 680.8. Must this clearance be adhered to or can this distance be shortened?
First, you have answered your own question. Additionally, it doesn't matter what 680.8 says since the NESC is the governing standard and, I assume, the serving electric utility owns the service drop. I agree, bury the service! :cool:

The clearances in the NESC are similar to the NEC. If it is an open wire service drop, the clearance is 23 feet. Also, the lowest point is to be calculated in the worst of circumstances (heat and loading) that would make the service drop sage to its lowest point. That is why the NESC is considered a performance document and not a prescriptive document. :smile:
 
If the service is buried it would have to pass within 5 feet of the inside wall of the above-ground permanent pool.
Does 05NEC 680.10. allow this?
Thanks.
 
smallfish said:
If the service is buried it would have to pass within 5 feet of the inside wall of the above-ground permanent pool.
Does 05NEC 680.10. allow this?
Thanks.

Since you stated it was a perminently installed pool, See NEC 680.20, that would lead you to NEC 680.10. NOT within 5' of the inside wall of the pool unless space is limited. See NEC 680.10
 
smallfish said:
Does 05NEC 680.10. allow this?
If it is in conduit, the NESC permits the installation. This is if the serving electric utility owns the service drop or service lateral and if I remember the NESC correctly. :smile: The NEC does not apply to the line side of the service point.
 