Service Entrance: 3 wire or 4 wire?

Status
Not open for further replies.
When installing a Meter with a disconnecting means (circuit breaker), my understanding is that you always install a 4 wire feeder to the house. I understand the breaker to be my service disconnect and the conductors to the house are FEEDERS.

An experienced electrical contractor has told me that you don't have to run the 4 wire feeder but that a 3 wire service entrance cable is allowed provided you do the necessary bonding and grounding at the house.

I can't seem to find the relevant Code requirement that would allow the use of a 3 wire entrance to the house after leaving the breaker in the meter base.

Please share your knowledge!!
 
We need one more detail, and that is: is the meter on the house or on a separate structure? If on the house, anything past the main disconnect is a feeder and must have a separate grounding conductor. If the meter is on a pole with a feeder to the house, you can do 3 or 4 wire per 250.32 (depends on if there are any other grounded metal paths between structures).
 
I'm assuming you're running a lateral to the house. You can use 3-wire for that. The house is a separate structure. All the grounding and bonding will be done at the house. You'll need a ground rod at the pedastal too, and bond the neutral there. Hope that helps.
 
nichols21vt said:
The meter will be on a pedestal about 10' from the pole and 100' from the house.
A couple of things here:

1) You can use either a 3-wire or 4-wire feeder to the house.
A) IF you use a 3-wire feeder, then you must ensure there is no other parallel grounded return path, such as a CATV cable or water pipe, etc.

b) In either case, you still have to have a main breaker or other suitable disconnecting means at the house, since your meter/disconnect is too far away to comply with the "within sight" rules (50 feet or less).

2) IF you are dealing with a mobile home, then all other bets are off, you have to use a 4-wire feeder, AND install a separate outside disconnecting means within 30 feet of the house.
 
kbsparky said:
b) In either case, you still have to have a main breaker or other suitable disconnecting means at the house, since your meter/disconnect is too far away to comply with the "within sight" rules (50 feet or less).

There is no "within sight" rule for panelboards and transformers.

Each structure needs to have a disconnecting means.
 