When installing a Meter with a disconnecting means (circuit breaker), my understanding is that you always install a 4 wire feeder to the house. I understand the breaker to be my service disconnect and the conductors to the house are FEEDERS.
An experienced electrical contractor has told me that you don't have to run the 4 wire feeder but that a 3 wire service entrance cable is allowed provided you do the necessary bonding and grounding at the house.
I can't seem to find the relevant Code requirement that would allow the use of a 3 wire entrance to the house after leaving the breaker in the meter base.
Please share your knowledge!!
An experienced electrical contractor has told me that you don't have to run the 4 wire feeder but that a 3 wire service entrance cable is allowed provided you do the necessary bonding and grounding at the house.
I can't seem to find the relevant Code requirement that would allow the use of a 3 wire entrance to the house after leaving the breaker in the meter base.
Please share your knowledge!!