New member here. I need some guidance on setting up a new service.
I have a 400 amp service from the utility to the meter base which will then feed (2) 200 amp disconnects. The utility requires the ground to be bonded in the meter. I have a #4 bare copper connected to 2 ground rods that will route into the meter base. The question that I have is with the neutral and the ground bonded in the meter, the neutral will then feed the neutral bar in the disconnects but should there also be a ground wire from the meter base the feeds a, separate from neutral, dedicated ground bar in the disconnect since the neutral and ground can only be bonded in one location. I have attached a diagram below that is similar but with only 1 disconnect.
Diagram
I have a 400 amp service from the utility to the meter base which will then feed (2) 200 amp disconnects. The utility requires the ground to be bonded in the meter. I have a #4 bare copper connected to 2 ground rods that will route into the meter base. The question that I have is with the neutral and the ground bonded in the meter, the neutral will then feed the neutral bar in the disconnects but should there also be a ground wire from the meter base the feeds a, separate from neutral, dedicated ground bar in the disconnect since the neutral and ground can only be bonded in one location. I have attached a diagram below that is similar but with only 1 disconnect.