Service entrance cable: Would (3) #3/0 THHN Copper fit in 1.5 inch rigid conduit?
fandi
Los Angeles
Electrical Engineer
Hello All,
I think the wires would fit in the mentioned conduit Per Annex C Table C.8 but my electrician said no. Is he right? It's a 10ft run from the 200A 2 gang meter to the weather head. I know #2/0 would be fine per the 83% factor for residential single family or duplex but the wires have been bought.
Thanks.
Hello All,
Thanks.
I mean he said the conduit needs to be bigger.
Did you ask him why since Annex C says it will fit?
Roger
According to that table either #2/0 or #3/0 will fit with three conductors so what's the problem?
My guess would be a POCO requirement. I know the the POCOs here don't allow anything less than 2-1/2" rigid (if using rigid) for a 200A service.
He said that's what he meant. I think it's confusing from my local POCO (Southern California Edison) since they would required bigger conduit than the one indicated in Annex C but their wires are still #2 (the same wires used for 100A service but now the service is upgraded to (2) 100A for two houses and the service planner said #2 on his side is still fine).
Hello All,
Thanks.
Why are you micro managing the electrician. Does this conduit go above the roof? If it does then it is a mast and you need 2" around here according to the power company.
Since the local SCE service planner only showed up once at the site and never replies to emails/phone calls, I find out the requirements from the latest SCE ESR (Electrical Service Requirements):
https://www1.sce.com/nrc/aboutsce/regulatory/distributionmanuals/esr.pdf
Section 8.2 page #27 reads: 200 A Service
Where the nameplate horsepower rating of any motor does not exceed 60 hp, 240 V or
125 hp, 277/480 V, a factory-bussed, safety-socket box with a 200 A rating shall be
installed.
The meter socket for 240 V service will be 5- or 7-clip, depending on the grounding of the
serving transformer bank. The meter socket for 277/480 V service will be 7 clip. Consult
your local Service Planning Office before purchasing or installing service equipment.
The maximum wire size or current-carrying capacity of the conductors installed in the
customer’s service raceway shall not exceed that of No. 3/0 wire and the conduit size of
any such raceway shall not exceed two inches
. The capacity of the customer’s service
switch is not limited under these conditions.