Service Entrance Cable
I agree that it is not suitable for inside premise wiring - however - it is only connected to the service equipment that is installed in the structure. Article 100 definitions: "Service equipment: the necessary equipment usually consisting of a circuit breaker(s) or switch(es) and fuse(s) and their accessories, connected to the load end of service conductors to a building or other structer, or an otherwise designated are4a, and intended to constitute the main control and cutoff of the supply." Is not the 200A disconnect and the 200A panel inside the structure considered Service equipment? The conductor is protected to the point of entrance by conduit as required by 300.5(D)(2). JM