Service entrance conductor meter pedestal disconnect requirements

Status
Not open for further replies.

Sharky18

Member
Location
Yorkville il us
Can anyone find the code section (2011 would be fine) that states the maximum distance a service entrance raceway may be installed before a meter disconnect ( fused on non) is required. Here's the catch. The raceway is 36' and installed under a concrete slab?
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
Can anyone find the code section (2011 would be fine) that states the maximum distance a service entrance raceway may be installed before a meter disconnect ( fused on non) is required. Here's the catch. The raceway is 36' and installed under a concrete slab?

I do not think that you will find it in the NEC. There are limits on how far service conductors (i.e. those with no overcurrent protection) can be run inside a building, which vary locally based on the AHJs interpretation of "nearest the point of entrance".

If it is under enough concrete, it is officially considered not to be inside the building.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Your Code references for the above are 230.70(A)(1) and 230.6
 