I am currently on a project in which the specified 2000Amp, 3PH, 480V main switch is to be fed with 4 sets of 500MCM (CU) from the utility co. transformer. Assuming the calculated loads (1500Amps) are in accordinance with Article 220 and 230.42. The 4 sets of 500MCM are only good for 1520Amps at 75c. My question is, does Article 230.90 or any other article apply to the over current protection of these service entrance conductors? We are being asked to proceed as specified although this does not seem like a good idea. In the event of an added piece of equipment the service entrance conductors have the potential to draw more than 1520Amps without tripping the 2000A switch