120/240 volt single phase service. A 6-unit apartment building has a calculated demand of 250 amperes. House meter plus 6 units - 7 meters each with a 100 ampere disconnect.
Contractor ran 350 kcmil aluminum in conduit from weather head to meter cabinet.
The 350 kcmil aluminum conductors terminate at an 800 ampere disconnect. Allowable ampacity of these conductors is 250 amperes in the 75 degree column.
I believe this is a violation and cited 2014 NEC section 230.42(B). The contractor is insisting that this arrangement is permissible. Am I missing something? The commentary in the handbook following section 230.80 reads "A single overcurrent device must have a rating or setting that is not higher than the allowable ampacity of the service conductors."
Thank you for any help.
Contractor ran 350 kcmil aluminum in conduit from weather head to meter cabinet.
The 350 kcmil aluminum conductors terminate at an 800 ampere disconnect. Allowable ampacity of these conductors is 250 amperes in the 75 degree column.
I believe this is a violation and cited 2014 NEC section 230.42(B). The contractor is insisting that this arrangement is permissible. Am I missing something? The commentary in the handbook following section 230.80 reads "A single overcurrent device must have a rating or setting that is not higher than the allowable ampacity of the service conductors."