Ok but plans call out first disconnect main service switchboard.
Maybe they are wrong. I dont know. As I said you will have to decide what, if anything is a meter disconnect.
Ok but plans call out first disconnect main service switchboard.
Please tell me that 2000A switchboard supplies more than just the one 30 amp circuit.I have plans that show it’s existing condition.
Plans don’t show who did what. No service point either.
Main breaker is main service switchboard 2000A
Cond #1 is (7) sets of 4#500kcmil +1#3/0G in 4 inch conduit. You see #3/0G is not sized per table 250.122 but it’s existing
Cond #2,#3 is 4#10 +1#10G in 3/4 inch conduit
Disco A is 30A fuse disco service entrance rated
Why did i read that in the voice of the architect?Are "ConA" and "ConB" on the load side of the "Main Fused Disconnect" ?
(I'll answer for you so this won't be one of your 10 post questions)
Yes they are on the load side of the "Main Disconnect" ergo, they are NOT service conductors.
I have to disagree on that.NO. Service point doesnt really matter. Meter disconnects are on the load side of the service point all the time.
Here is one of your previous threads on the topic:
Utility disconnect not service disconnect
I have project new building gas station convience store in which utility transformer secondary conductors enter non fuse Disconnect #1 outside convience store building then go to new utility meter/Ct then inside nearest entrance drop to 1000A 208V three phase panelboard. The 1000A panelboard...forums.mikeholt.com
Isnt that what I said?I have to disagree on that.
Simple 200 amp 480/277 wye service can have service point be at the point of attachment of service drop conductors. That puts the metering and cold sequence disconnect all on load side of service point and subject to NEC requirements. The POCO will put a lock/seal on the cold sequence disconnect and the meter socket, but they are still customer owned and likely maintained at customer expense equipment, you just have extra involvement with POCO to be able to break the seal that is providing tamper evidence for their cash register that is plugged into the meter socket.
Too early I guess, and apparently my eyes read something other than what you wrote.Isnt that what I said?