Service Entrance Conductors Disconnecting means?

JMEG

Member
Location
Texas
Occupation
Master Electrician
I will be installing an electrical service to 2 separate structures, a house and a shop. The utility company has set a 320A meter pedestal approx. 175' away from each of the structures. They utility company is requesting I put a main disconnect next to the meter. My question to the group is, will I need to install a grounding bonding jumper at this main disconnect 175' away from each of the structures? Or can I just install bonding jumper at the main disconnects I will be installing on each of the structures?
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Is your disconnect at the meter ahead of the meter or load side ? Fusible or N/F ?
 

JMEG

Member
Location
Texas
Occupation
Master Electrician
Is your disconnect at the meter ahead of the meter or load side ? Fusible or N/F ?
When I install it it will be on load side of meter base, I haven't decided if it needs to be fusible or not? I am wanting to run a 3 wire service URD to another disconnect that will be on the structure. From what I read in code you want your bonding jumper at entrance of structure. Im just trying to keep it with in code but I'm not finding info on this situation.
 

JMEG

Member
Location
Texas
Occupation
Master Electrician
I don't feel I even need a disconnect near the meter base, but that's what the utility company is asking for.
 