Service Entrance Conductors Disconnecting means?

Merry Christmas

JMEG

Member
Location
Texas
Occupation
Master Electrician
Service will be feeding a dwelling, and a shop.
I wouldn't. I would see if I could run 3 wire. It's really a much better system: less equipment, less connections, better fault return path.
I totally agree with you, should I use fuses if I were to decide to go 3 wire to each of the separate structures?
 

JMEG

Member
Location
Texas
Occupation
Master Electrician
I don't think the POCO would say anything if I ran 3 wire or 4 wire, I don't think they even look or care about that... This is in a rural area with no inspections. But I want to keep it in code.
 

JMEG

Member
Location
Texas
Occupation
Master Electrician
I wouldn't. I would see if I could run 3 wire. It's really a much better system: less equipment, less connections, better fault return path.
I don't think the POCO would say anything if I ran 3 wire or 4 wire, I don't think they even look or care about that... This is in a rural area with no inspections. But I want to keep it in code.
 

Attachments

  • 320A meter.jpg
    320A meter.jpg
    312.9 KB · Views: 8
Service will be feeding a dwelling, and a shop.

I totally agree with you, should I use fuses if I were to decide to go 3 wire to each of the separate structures?
My idea/preference would be a meter only at the remote pedestal. You would be using 230.40 exception number three to run a set of service conductors (3 wire ) to each building. I don't remember if you said what code you were on but the dwelling might require the exterior emergency disconnect. The shop would not and you can put a main breaker panel on the inside at the nearest point of entry.
 