Look at the definition of "service entrance conductors" (either overhead or underground). I believe that fits as it uses "service equipment" and not "service disconnect"In this unusual scenario where the service OCPD is in a separate enclosure immediately adjacent to the service disconnecting means, it is unclear how to label the conductors between the two enclosures. They are not service conductors, as that definition says "The conductors from the service point to the service disconnecting means."
Good point. So the conductors between the service disconnect and the separately enclosed service OCPD are definitely service entrance conductors, definitely not service conductors, and may or may not be a feeder, depending on how you interpret that definition.Look at the definition of "service entrance conductors" (either overhead or underground). I believe that fits as it uses "service equipment" and not "service disconnect"
The definitions are definitely flawed. It appears that "service entrance conductors" are a portion of "service conductors", but "service conductors" only go to the service disconnect, while "SEC" go to the service equipment.Good point. So the conductors between the service disconnect and the separately enclosed service OCPD are definitely service entrance conductors, definitely not service conductors, and may or may not be a feeder, depending on how you interpret that definition.
Cheers, Wayne
Whoops, I withdraw post #43, as you point out the SEC definition requires the conductors to be service conductors, so they stop at the service disconnect. Conductors between the service disconnect and the service OCPD are neither service conductors nor SECs.The definitions are definitely flawed. It appears that "service entrance conductors" are a portion of "service conductors", but "service conductors" only go to the service disconnect, while "SEC" go to the service equipment.
That suggests to me that we really should treat the two enclosures as one somehow.Whoops, I withdraw post #43, as you point out the SEC definition requires the conductors to be service conductors, so they stop at the service disconnect. Conductors between the service disconnect and the service OCPD are neither service conductors nor SECs.
Well its not consistent, so I dont dont see how you can conclude one way or the other. The definition of SEC says "service equipment".Whoops, I withdraw post #43, as you point out the SEC definition requires the conductors to be service conductors, so they stop at the service disconnect. Conductors between the service disconnect and the service OCPD are neither service conductors nor SECs.
Cheers, Wayne
Nice discussion here. Just to recap, do we have definitive answers about a disconnect without OCPD (post #15 , see sketch OPTION 1. Reposted here):
1 & 2) Does this disconnect require a neutral bar bonded to the case (MBJ)?
3) If yes, is this then considered a "service disconnect"?
4) Is a separate grounding conductor (in addition to the neutral) required on the load of this disconnect?
1&2. Yes
3. Yes, unless it is an emergency disconnect as permitted in the 2020 and 2023 NEC.
4. If it is an emergency disconnect, no. If it is anything else, yes
To the neutral, of course, just like any supply-side enclosure.Just for my own knowledge, how is grounding / bonding handled in an emergency disconnect?
No, because there is no EGC/EGC system yet.I'm assuming the case also needs to be bonded to neutral but then wouldn't you need a neutral bar for that and wouldn't this connection be considered a MBJ?
Note everything on the supply side of the service disconnect is bonded to neutral. It's basically the same thing as a MBJ except it is not called an MBJ. An MBJ is a specific type of "service bonding jumper" that is in the service disconnect.
I have a slightly different take from the other answers so far today. Article 230 tells us we must have a "service disconnect". 230.82 tells us what limited set of equipment may be installed on the utility side of the service disconnect, e.g. meters as per 230.82(2).Nice discussion here. Just to recap, do we have definitive answers about a disconnect without OCPD