Service entrance conductors run through panel

Status
Not open for further replies.

ponycar290

New User
Location
Tennessee
Occupation
Electrician
Installed an service entrance rated ATS next to a main breaker panel. Installed 2 - 2" conduits between panel and ATS, ran un-spliced service entrance conductors through one conduit to ATS main breaker, then load side conductors back through second conduit to main breaker. Grounds and neutrals separated accordingly. Inspector is not allowing the service entrance conductors to be run though the panel to the ATS but won't provide code article that it violates. A little help please?
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
Have the inspector explain what in 230.7 prohibits your installation.
"230.7 Other Conductors in Raceway or Cable. Conductors
other than service conductors shall not be installed in the same
service raceway or service cable in which the service conductors
are installed."

Your use of two separate conduits addresses his concerns.
 