When is is required to install a duct bank for conduits under the building slab? Does it have anything to do with the spacing of the conduit? Is it o.k. to install conduits on top of each other without any spacing?
iwire Moderator Staff member Location Massachusetts Sep 10, 2006 #2 Ben Trueblood said: When is is required to install a duct bank for conduits under the building slab? Click to expand... I think we should clear up what you veiw as a 'duct bank' In my experaince that genrally means a group of conduits installed on racks with enginered spacing requirments encased in concrete Does it have anything to do with the spacing of the conduit? Click to expand... In my opinion it may or may not. Is it o.k. to install conduits on top of each other without any spacing? Click to expand... You already know the answer to that, you must maintain spacing. How much space is up to debate but IMO it is always more than none.
Ben Trueblood said: When is is required to install a duct bank for conduits under the building slab? Click to expand... I think we should clear up what you veiw as a 'duct bank' In my experaince that genrally means a group of conduits installed on racks with enginered spacing requirments encased in concrete Does it have anything to do with the spacing of the conduit? Click to expand... In my opinion it may or may not. Is it o.k. to install conduits on top of each other without any spacing? Click to expand... You already know the answer to that, you must maintain spacing. How much space is up to debate but IMO it is always more than none.