Service entrance grounding question

Status
Not open for further replies.

ggunn

PE (Electrical), NABCEP certified
Location
Austin, TX, USA
Occupation
Consulting Electrical Engineer - Photovoltaic Systems
We have a situation where we need to place a new service disconnect on the outside of a house. Presently, the service disco is the main breaker on the MDP inside the garage, but under "you touch it you fix it" when we interconnect our PV system we'll have to bring the service up to local code, which now requires the service disco to be outside.

Here's the rub, bub. It's an older service and the MDP is big and jam packed. The ground and neutral bars are bonded, and the circuit grounds and neutrals are randomly distributed between them. Unbonding the bars so we can bond G to N in the new disco will require a massive removal of a rat's nest of wiring from atop the N and G bars in the MDP to get to the jumper, as well as moving all the G's to the G bar and N's to the N bar.

My question is this: Is there any provision in the code which would let us leave the N to G bond in the MDP and have them unbonded in the disco? I'm pretty sure what the answer is but I had to ask.
 
Last edited:

ggunn

PE (Electrical), NABCEP certified
Location
Austin, TX, USA
Occupation
Consulting Electrical Engineer - Photovoltaic Systems
You are correct in your frear. About the only thing you might be able to do is move all the breakers outside and use the old MDP as a junction box.
That's what I figured. Moving all the breakers outside would be worse.
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
You're basically facing the same issue that you would when adding a whole-house generator and transfer switch.
 

ggunn

PE (Electrical), NABCEP certified
Location
Austin, TX, USA
Occupation
Consulting Electrical Engineer - Photovoltaic Systems
You're basically facing the same issue that you would when adding a whole-house generator and transfer switch.

It's not my first rodeo. :D

I knew it was a very long shot, but if there were some language in the NEC that would have allowed me to leave the N-G bond in the MDP I didn't want to miss it because I didn't ask.
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
Then you're back to asking your inspector "What would I have to do, or not do, to be able to leave that part of it as it is?"

I would actually ask.
 