Grounded conductor is connected to earth or it wouldn't be called a grounded conductor.

But how much resistance to earth is acceptable? NEC alone doesn't really give us much for limitations other then a single ground rod has to be less then 25 ohms or be supplemented.

What if it's 265 ohms?
 
What if it's 265 ohms?
If it is a single rod you have to drive a second rod to comply with NEC. Chances are it doesn't get lowered by much though. Now if you have some specification or other desire to be below a certain level - then you have some more work to do.

And if you just drive two rods to begin with - to comply with NEC you are done, no requirement to even measure it. It could still be 265 ohms.
 