kwired
Electron manager
- NE Nebraska
- EC
50 KVA may have more than 10KA available, particularly if you have a really short run of supply conductor to the device in question. Depends on actual impedance of the transformer. Over 50 feet shouldn't be any problem though conductors will have enough resistance to drop the available current at load end.Based on the sound of it, I doubt the available fault current is very high. Are these smallish pad mounts, like 25-50 KVA?