Sparky if you can give a little more detail it would help.

Are you using it as a mast?

The basic requirements are in 344.30 and Table 344.30(B)(2).
 
You may also have additional POCO requirements if you're using the RMC as a service mast. Check with them if that's the case.

Oh, and welcome to the forum! :smile:
 
RMC riser used as service entrance mast.

RMC riser used as service entrance mast.

the RMC riser is being used a service entrance mast. I remember seeing the strapping code somewhere, but now i cannot find it.
 
POCO's here determine that.

Last support is 30 or 36" from top of weatherhead. Mast brace if eaves, 3/8" thru bolted if unistrut or 2 hole strap.

Riser over 36" must be back braced with 2, 3/4 emt feild built braces attaching to the point of attachment and thru bolted through a rafter.

No point of attachments over 6' above roof (new rule)
 
=sparky= said:
the RMC riser is being used a service entrance mast. I remember seeing the strapping code somewhere, but now i cannot find it.
What power company (POCO)?

Usually the POCO has more stringent support requirements. Your POCO, if they have a website, may have the requirements accessible over the internet.
 