yucan2
Senior Member
- Location
- Just south of Chicago
Is it legal to place a service entrance rated transfer switch ahead of a triple stack modular meter assembly? Im looking to provide a gen service to a single premises which consists of one 200A service and two 100A services.
We've never installed a service rated ATS ahead of any metering but it does beg some thought.
I would think that if you get the local POCO involved and provide a one line clearly showing your proposal, it could possibly fly. The reason being is that we frequently install multi-tenant metering that is served from a single or multiple disconnects before the tenant meters. What you propose is quite similar.
In addition, if it does fly, then only one ATS would be required, as one would not normally monitor just one service in this scenario, but the entire location, as the loss of power to just one premises would probably indicate some other problem specific to that premises and a problem that the generator would not resolve and could actually compound.
Also in this scenario, a tenant being disconnected from the utility (removal of the meter), for whatever reason would not be seen as an outage by the transfer switch. The ATS is looking at incoming utility power, nothing else.
One additional note, obviously in this setup, the generator must be capable of carrying the full available load.