Service entrance rated

Status
Not open for further replies.

shaw0486

Senior Member
Location
baltimore
Hello,
I am installing a generator and I am curious when does the transfer switch have to be service rates? Also when does a panelboard have to be services rated othere than when it is obviously a service?
 

ceb58

Senior Member
Location
Raeford, NC
Hello,
I am installing a generator and I am curious when does the transfer switch have to be service rates? Also when does a panelboard have to be services rated othere than when it is obviously a service?

It doesn't have to be service rated. A service rated transfer switch has the service OCP/disconnect built in to the unit. You can install a non service rated switch but there must be a service rated disconnect between the meter and ATS.
 