Just curious, if the neutral buss bar is connected to the ground buss bar at service equipment, then wouldn't neutral current flow through the service enclosure as a return path back to the utility source?
So if there is neutral current flowing through service equipment enclosures, 10A, 20A, 100A, etc... this isn't harmful if someone touches the equipment?
So if there is neutral current flowing through service equipment enclosures, 10A, 20A, 100A, etc... this isn't harmful if someone touches the equipment?
The current does not flow to the grounding electrode in earth as a path
We cannot use it as a path but it is one.
I am keeping the conversation to unbalanced load return path & power source grounding point -- of course the electrode system is the path to direct induced voltage on wiring systems from lighting strikes to earth
But you seem to be saying if I drive a ground rod into the earth and connect it to a neutral conductor carrying unbalanced current there will be no current flow to earth. :?
the flow goes back to the source & earth is not a source -- the same reason the electrode will not trip a breaker -- show me a diagram of your thoughts -- simply if there is a current flow & your break the connection/ tap the buss & you will see an arc occurs. now take you electrode conductor & do the same thing/ no arcs -- now we can get into the resistance differentials & path continuity & really have conversation.
Earth may not be THE source but because there's another electrode connected to the neutral at the service transformer, the earth is a path... albeit a higher impedance path than a nominally functional neutral conductor, but it is a path (though not to be considered one under Code) and will conduct some amount of current.the flow goes back to the source & earth is not a source..
the flow goes back to the source & earth is not a source --
See the attachment. If there unbalanced neutral current returning to the utility source, the neutral is connected to the ground bar which is connected to the service equipment metal case. So some current should be flowing here (I think?)....
Per attachment, no current is flowing "through" the enclosure. The grounded service conductor and earth through the two electrode systems are the only paths depicted.See the attachment. ...
See the attachment. If there unbalanced neutral current returning to the utility source, the neutral is connected to the ground bar which is connected to the service equipment metal case. So some current should be flowing here (I think?).
Edit: Hmm there is a image limit of 620 x 280 which makes the picture almost illegible. I can't upload it.