electrofelon
Senior Member
- Location
- Cherry Valley NY, Seattle, WA
Just curious, if the neutral buss bar is connected to the ground buss bar at service equipment, then wouldn't neutral current flow through the service enclosure as a return path back to the utility source?
I have a little bit of a different take on it. Now as others have said, even with no common metal water pipes connected back to the transformer thru other services, and just a rod or two, you will have some current getting back to the source via dirt. That isnt really what the OP was asking or questioning. Note that the GEC is required to connect to the neutral conductor or its buss. I dont see current generally flowing through the service enclosure/cabinet unless something is not done correctly. I suppose where you have a separate EGC and neutral bus and metal frames of utilization equipment are sitting on dirt/concrete or connected to metal water pipes, you would then have a very small amount of current flowing through the cabinet.