If a service coming to a bldg comes to a main lug only distribution panel ( mdp) and it has 8 means of disconnect but is only using 6 to feed other panels is it compliant?

Sent from my GT-N5110 using Tapatalk
 
No, six moves of the hand must remove all power from the building, outside of exceptions for things like fire pumps, emergency systems, systems with different voltage, etc.
 
What are the two that don't feed other panels? Main for other sections in same gear? Main for primary of transformers? Both of those would need to be counted in the six disconnect rule.
 
What are the two that don't feed other panels? Main for other sections in same gear? Main for primary of transformers? Both of those would need to be counted in the six disconnect rule.

What if they are spare breakers and do not energize anything?
 
That is my concern. This is a remodel. The xfmr sits on the pad and the SEC feeds down to the below ground level floor with offices and the electrical room where the service equipment is. The enclosure takes up almost the whole room.

Sent from my LGLS770 using Tapatalk
 
If the spaces were there but not the breakers, I would say no problem.
With the breakers there but unconnected I would not expect the AHJ to accept a situation where someone has to read the stickers to see which six throws will disconnect the service. Maybe if the breakers were locked in the off position?
But why not just remove them?
 
I may be using the wrong terminology. They are fused disconnects. (buckets)
I can remove them. Then Ill have to find the metal blanks to cover the spaces.

Sent from my LGLS770 using Tapatalk
 
I may be using the wrong terminology. They are fused disconnects. (buckets)
I can remove them. Then Ill have to find the metal blanks to cover the spaces.

Sent from my LGLS770 using Tapatalk
I might ask the AHJ whether it would be acceptable to lock them in the Off position. Likely the answer would be no, but it would not hurt to ask.
 
If the spaces were there but not the breakers, I would say no problem.
With the breakers there but unconnected I would not expect the AHJ to accept a situation where someone has to read the stickers to see which six throws will disconnect the service.

Why would you expect the next electrician to violate the code?

Why couldn't the inspector fail it at that time?
 
I may be using the wrong terminology. They are fused disconnects. (buckets)
I can remove them. Then Ill have to find the metal blanks to cover the spaces.

Sent from my LGLS770 using Tapatalk

Don't create a violation to appease an inspector that has no code reason to fail this job.
 