Service Feeder for non continuous duty motor

Status
Not open for further replies.

skyline77

Member
Hi,
For sizing a service feeder for a non dwelling building with several loads.
An elevator motor per Table 430.22(e) the last column is "Continuous Rated Motor"
Is it the same as continuous duty?
In sizing the elevator motor should I consider Continuous Rated Motor i.e. 140%??
 
First, a service and feeder are different. Its either one or the other. But the connected load will be same. One difference would be size of neutral.
Continuous duty motors are sized at 125%.
I have never done a calvulation for elevator motor, what design is it?
 