S steveonb Member Aug 20, 2008 #1 I have a five gang meter center, with 5 200amp 3 phase units, how do I size the feeder to the meter center?
I have a five gang meter center, with 5 200amp 3 phase units, how do I size the feeder to the meter center?
iwire Moderator Staff member Location Massachusetts Aug 20, 2008 #3 Is it a main breaker or main lug meter pan? What is the calculated load?
iwire Moderator Staff member Location Massachusetts Aug 20, 2008 #5 So 10,800 x five convert to amps for your voltage and that is the minimum conductor rating if it is a multiple service disconnect installation.
So 10,800 x five convert to amps for your voltage and that is the minimum conductor rating if it is a multiple service disconnect installation.