Re-approaching a situation that had been discussed earlier but one on which I have now confused myself.
Single family residence, 120/240 volt 3 wire service.
Per 310.15(B)(6) I'm using a 600 al to feed a 400 amp meter socket.
From the load side of the socket I'm using installing XHHW AL service conductors to feed two 200 amp feed thru panels being used as service disconnects. As these individual service condcutors are not carrying "all loads associated with the dwelling", I size them per 310.16. In this situation my computed load on each panel is less than 180 amps, so I use a 4/0 XHHW utilizing 240.4(B).
From my two outisde service panels I extend coanductors into the house to feed two interior panels. I elect to use AL SER cable.
What size SER cable would be required under the '08 Code ?
Single family residence, 120/240 volt 3 wire service.
Per 310.15(B)(6) I'm using a 600 al to feed a 400 amp meter socket.
From the load side of the socket I'm using installing XHHW AL service conductors to feed two 200 amp feed thru panels being used as service disconnects. As these individual service condcutors are not carrying "all loads associated with the dwelling", I size them per 310.16. In this situation my computed load on each panel is less than 180 amps, so I use a 4/0 XHHW utilizing 240.4(B).