Hey Guys.
First post - Here is a little background info on a question that I would like to present to the community.
I've been asked to install a battery charger for an electric floor sweep machine inside an industrial warehouse. The industrial engineer wants to save money on the installation by utilizing an existing 60A welding distribution system consisting of (2) separate disconnects with outlets nippled directly to the disco's enclosure. The engineer is willing to abandon (1) of the outlets in favor of connecting the new piece of equipment. The service is 3 Phase, 480V protected by a 60A distribution breaker. The new piece of equipment is 3 Phase, 480v @ 5.5A FLC. I've considered two different options to try and make this installation right.
1) Jumping through hoops in an attempt to make things right - I would remove the outlet and nipple in an 8X8X4 J-Box. Install a 60A rated 3P fuse holder w/#6 THHN inside the J-Box. Install fuse holder reducers to allow the installation of fuses below the 30A rating. - This would get me down to traditional wiring methods?
2) This one is "stretching" things a little - Not remove the 60A outlet and just simply "whip" the charger with a #6 SJO and male plug. Would this cover me with the "Cord and Plug Rules" ???
Thanks for reading and submitting any replies.
Randy
First post - Here is a little background info on a question that I would like to present to the community.
I've been asked to install a battery charger for an electric floor sweep machine inside an industrial warehouse. The industrial engineer wants to save money on the installation by utilizing an existing 60A welding distribution system consisting of (2) separate disconnects with outlets nippled directly to the disco's enclosure. The engineer is willing to abandon (1) of the outlets in favor of connecting the new piece of equipment. The service is 3 Phase, 480V protected by a 60A distribution breaker. The new piece of equipment is 3 Phase, 480v @ 5.5A FLC. I've considered two different options to try and make this installation right.
1) Jumping through hoops in an attempt to make things right - I would remove the outlet and nipple in an 8X8X4 J-Box. Install a 60A rated 3P fuse holder w/#6 THHN inside the J-Box. Install fuse holder reducers to allow the installation of fuses below the 30A rating. - This would get me down to traditional wiring methods?
2) This one is "stretching" things a little - Not remove the 60A outlet and just simply "whip" the charger with a #6 SJO and male plug. Would this cover me with the "Cord and Plug Rules" ???
Thanks for reading and submitting any replies.
Randy